FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

VRF Outdoor Fan Motor - Electric Efficiency

Hi! Many local LEED Consultants have the same doubt related to VRF Systems when modeling per ASHRAE 90.1-2007 and regarding mandatory provisions. The first one is which is the system we must use as equivalent of VRF for the proposed building and the second one is do the Fan Motor of the Outdoor Units Compressors need to comply with the electric efficiencies per Table 10.8?. We know that single-phase motors are exempt but what about three-phase ones?. Thanks so much for your help.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 01/07/2014 - 20:53

Not sure if I am interpreting the first part of your question correctly so I will provide three answers. If you mean which is the equivalent baseline system - The baseline system is always defined by G3.1.1. VRFs tend to be all electric systems so use the electric column in Table G3.1.1A. Depending on the area and number of floors it should be a System #4, #6 or #8. If you mean how do we model a VRF system if the software does not do so explicitly - You should model VRF systems with software that can directly model those systems. If this is not possible you will need to use a published work around or provide a thorough narrative describing how you have modeled the system. If you mean what is the mandatory VRF minimum efficiency since it is not in the 6.8.1 tables - Since it is not listed, technically there is no mandatory minimum. However, ASHRAE 90.1-2010 does list minimum efficiencies for these systems which could serve as a guide. I would not be at all concerned about the fan motors in the outdoor units. These fans are not scrutinized for compliance with this mandatory provision.

Tue, 01/07/2014 - 20:58

Marcus, thanks so much! you have just answered all my questions and cleared all my doubts. I was already aware of ASHRAE 2010 requirements regading VRF so we will look forward for this standard in order to get ready for LEED v4. Thanks again,

Tue, 01/07/2014 - 21:37

You are quite welcome.