FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Voltage drop

Folks, Is there any exception for the 2% and 3% voltage drop? We are working on a subway station and we were able to achieve 3,5% to the feeders and 3% to the to the branch circuits. Achieve 2% and 3% will increase construction cost significantly according to the electrical system designer. Is there any percentage allowance? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/13/2012 - 16:06

There do not appear to be any exceptions to this mandatory provision in 90.1.

Thu, 12/13/2012 - 15:52

Hi Marcio, This topic was explored by the EA TAG a few months ago. While they didn't feel that it was appropriate to make an overall exception to the requirements, they did decide on what they felt was a fair compromise. From LI #10218: "...the mandatory provision of ASHRAE 90.1-2007/2010 Section 8.4 will be met as long as the total voltage drop does not exceed 5%." This may not be helpful to your situation, but you should be aware that it is out there. Thanks