CI-v4.1 EQc8:Quality Views

View to indoor garden

Hi LEED experts, about "Views into interior atria may be used to meet up to 30% of the required area". Does that mean a room with no view to the exterior but has a view to the indoor garden, can be counted as the area with view? and we only count 30% of this room area, instead of 100% right? Thanks for your comments.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/22/2022 - 13:15

It does mean that room would be counted.  You would count 100% of that room area, but it can only count toward 30% of the total views area. In other words, 70% of the area you're counting as having a view has to have a view to the outside. 