We are working with a project located in a 3C climatic zone. Therefore, our building’s main entrances include a vestibule as mentioned in section 5.4.3.4.
Furthermore, inside the building there will also be small enclosed vestibules that separate the office areas from the bathrooms. Therefore, people will be crossing through these small rooms that work as vestibules to access the bathrooms all day.
Should these spaces require to be ventilated with a minimum outdoor air supply? Or can we just leave them without ventilation since they are merely a transition space where people will be for very short periods of time throughout the day.
Thanks in advance!
Gabriela Crespo
BECxP, CxA+BE, LEED AP BD+C, O+MRevitaliza Consultores
20 thumbs up
October 26, 2017 - 2:35 pm
Hi Angel!
Yes, vestibules are required to have ventilation even though they are transition spaces. It has to do with the definition of occupied, occupiable and non occupied spaces.
I hope this helps!
Francesco Passerini
R2M Solution Srl16 thumbs up
December 15, 2017 - 5:11 am
Hello, could air extraction in the spaces between corridor and restrooms be acceptable? In the corridor the supplied air exceeds the required air flow rate therefore I would present that as an engineering ventilation.
Best Regards
October 30, 2018 - 4:41 pm
Francesco,
Did you ever receive a response to your question? I am in a similar situation. Thanks!