Ventilation for Shipping / Receiving (Local law vs ASHRAE)

Hi,

We have a Distribution centre (Nothing Hazardous) of 1000m² with 10 people. The ventilation requirement by ASHRAE is Area- (1000*0.6)+ People (10*5) =  650 l/s. The local bylaw says it is around 4 l/s per person (No area is needed for ventilation) = 40 l/s. There is a huge difference in the ventilation requirement.

Can we design the ventilation requirement to comply with local law as ASHRAE's requirement is energy intensive? Or is there a special clause under ASHRAE in which we can use only the ventilation requirement of people?

- Prethvi

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/15/2023 - 14:16

No. You need to meet ASHRAE 62.1.

Tue, 10/17/2023 - 04:05

Hi G.J., Where is your project located? Projects in Europe may use Arbeitsstaettenrichtlinie ASR 5 as a local equivalent to ASHRAE Standard 62.1-2010, natural ventilation procedure.