If an AHU is serving more than 1 space and these spaces are of different occupancy/usage patterns (ie serving partly an office, a corridor, and an auditorium), how do we input the space assigned to this particular AHU? Do we assume it to be serving the biggest load? or the most used? Or do we enter it once for each of the spaces - how do we account for its capacity for each space in the Ventilation Rate Procedure?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $... »
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
July 12, 2010 - 11:35 pm
I would enter it for the biggest space, or the space that is most relevant in determining its rate.
Jenny Carney
Vice PresidentWSP
LEEDuser Expert
657 thumbs up
September 15, 2010 - 1:01 pm
Pablo - The 62MZ calculator downloadable from LEED Online lets you account for all the different spaces served by a single AHU. You build up the total OA requirement from the OA required for each of the different space classifications served by that AHU.