Dear LEED Team, just calculated the ventilation rate according the ashrae 62.1.2007 for a office building and now really wonder about the low outdoor air rate: Density: 100 ft²/person (net occupiable area in zone) OA per person: 5 cfm OA per m²: 0,6 cfm/ft² Combined OA per person: 5 cfm + 0,06 cfm/ft² x 100 ft² = 11 cfm/person Compared to the European standard with around 20 cfm this seems to be very less. In cubicle offices with lower density it even gets worse. At the same time the ASHRAE recommends a CO2 level of 1000ppm - which is not reachable with the given 11 cfm/person. So, how can this be explained?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/12/2014 - 14:27

Hello- Although still widely cited, the 1,000 ppm CO2 concentration is an old ASHRAE reference from 62.1-1989. I don't believe 62.1-2007 refers to that CO2 level. ASHRAE has converted to a dual component method of recommended minimum ventilation rates, based on air flow per unit area plus air flow per person. Apparently, the new ventilation rates recommended are considered adequate even though they can result in CO2 concentrations well above 1000 ppm.

Wed, 03/12/2014 - 14:45

Marco, you calculated Vbz, but you need to calculate Vot to determine how much OA is needed for compliance.