Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

Ventilation for parking garage

Hi All, I have a question about a project under LEED certification. We are designing the ventilation of one floor below-grade parking garage, situated below an open area adjacent to an office building. The garage floor plan is of rectangular shape. There are no Full Time Equivalent in the parking garage (guard stations, and/or other occupied/occupiable spaces are not located in the garage, so the whole space is only for the purpose of parking and circulation). There is no mechanical ventilation. Openings for natural ventilation are provided. We would like to understand whether our design can be considered an alternative compliance path to ensure indoor air quality compliant with "Minimum Exhaust Rate" Table 6-4 of ASHRAE 62.1:2007 Note C " Exhaust not required if two or more sides comprise walls that are at least 50% open to outside". Openings for natural ventilation are evenly distributed on the roof of the garage (grade level). The overall surface of these openings to the outside is greater than 50% of the overall surface of two side walls. Also, an electronic CO monitoring system provides an alarm if the threshold of CO concentration achieves/exceeds 25ppm. As a result of an alarm, access to other vehicles to the garage is temporarily impeded until dilution/exhaust of contaminant through natural ventilation lowers CO concentration below the threshold. Can we implement such a compliance path in lieu of mechanical ventilation? Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/21/2015 - 14:13

Hi Fabio, unfortunately, your design does not comply with the requirements of ASHRAE 62.1. The reason that they specify two sides with more than 50% rather than 25% wall area, is because they count on crosswinds ventilating the space. You should add the mechanical ventilation. Also, in my opinion, relying on buoyancy of CO vs air to ventilate the space is not a good design practice. The level of CO may rise to unsafe levels and it is unlikely that the people going in to get their cars will decide to wait it out. If that case were to happen during a busy period, I could not imagine an owner who would prefer a closed garage in lieu of having simply installed the mechanical ventilation in the first place.

Mon, 08/31/2015 - 14:02

Thank you so much!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.