I’m having some doubts on how to define the stormwater volume treated by different types of vegetated areas since in Brazil we don’t have any study related to it. 1- If my project has a flat vegetated area, can I consider that 90% of the stormwater will be treated by infiltration (considering this area has a 0.1 runoff coefficient) and that 100% of TSS of the infiltrated volume will be removed? 2- If my project has a green roof (4-8 inches), can I considerer that 70% of the stormwater will infiltrate and that 100% of TSS of the infiltrated volume will be removed, even if this volume will not be retained in this area, i.e., the volume infiltrated will be drained to public sewers after the soil saturation?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/30/2012 - 20:30

Patricia, on item 1 I agree with your calcuations. On item 2, it gets more complicated since all green roofs are different—I think you could use some input from a civil engineer on that.

Wed, 10/10/2012 - 15:47

Hi, two questions that came to my mind when reading the above comment: 1 -when calculating the treated run-off, do you include the water volume in the calculation that infiltrates into the ground/evaporates and also the volume that leaves the area? I mean, in case of a vegetated area where runoff coefficient is 0.1, do you get the credit without any additional BMP, saying that the 90% is treated with 100% efficiency, equaling a 90% average; or do you only get the credit if the actual runoff (10% of total rainfall) flows through a BMP of 80% efficiency before leaving the site? 2 - What is the difference between the removal efficiency of the flat vegetated area and i.e. a grass swale? Grass swale should capture water and infiltrate it into the ground - however, average efficiency is only 60% according to EPA. Can water infiltrating into the ground really be considered to remove 100% TSS?

Wed, 10/10/2012 - 16:04

1.The curve number used to generate a runoff volume already takes into account the volume that infiltrates. A higher CN produces a higher runoff volume. 2. Your question regarding removal efficiencies is a long-standing argument with any regulatory agency. 85% TSS is typically what I see/use with any type of vegetated BMP. Definitely not 100% with any type of open-channel flow.

Wed, 10/10/2012 - 16:17

Thanks Michael, So you say that in question 1 that you do have to treat the volume of runoff, even if the infiltration is around 90%?

Wed, 10/10/2012 - 17:24

If you are infiltrating 90% of the sites runoff, through a BMP with 80% TSS removal, you are good.