VAV system required for small DX?

I am researching option 1 for Advanced building requirements. We are working in a 1 story industrial park and are installing new 10 ton and below DX RTUs. We are meeting all the efficiency requirements, but I am uncertain if 3.10 Variable Speed requires VRV system? Or is a constant volumn DX RTU design acceptable?

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/13/2012 - 17:48

If your individual unit fan motor horsepower is greater than 5 hp then you would need to comply with 3.10. If less than 5 hp make sure to point that out in your documentation.

Tue, 05/15/2012 - 22:04

I have a similar issue where the pollution control in the unit is a constant volume fan and needs to be that way for exhaust and pressure requirements. We don't have a VAV fan that is 5hp or more. Do we document this in Special Circumstances?