Appendix G3.1.3.13 says "Minimum volume setpoints for VAV reheat boxes
shall be 2.15 L/s·m2 of floor area served or the minimum ventilation
rate, whichever is larger"
When you have a HVAC system which serves spaces which are required in the baseline to have demand controlled ventilation should the minimum volume set point for VAV be dynamic based on the minimum ventilation at any point or set based on the design minimum ventilation rate (e.g 7.5 cfm/person at peak occupancy).
Thanks
Vicky
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
May 27, 2014 - 11:53 am
Above the G3.1.3.13 minimum setpoint the VAV should be dynamic assuming the ventilation requirement is higher than this minimum. As the occupancy increases the ventilation rate goes higher up to the maximum value. If the ventilation requirement decreases below the G3.1.3.13 minimum then the volume setpoint must be maintained.