FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

VAV FAN POWER BOX MODELING

I am working on a project where the base line hvac system is type 6 VAV with fan power boxes. ASHRAE 90.1 requires the fan power box CFM to be sized at 50% of the peak CFM at 0.3 W/CFM. There is no guidance in 90.1 user manual on how to comply with this requirement, further more when we asked the modeling software help line they said that it can’t be done and that the software is automatically sizing the fan power box CFM at 50% of the system heating CFM not the cooling CFM. This comment keeps coming almost on every project with this type of system. Any input on how to deal with this issue?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/21/2013 - 20:28

What software are you using?

Tue, 05/21/2013 - 20:40

trace 700

Wed, 05/22/2013 - 02:13

I am also creating baseline with system-6. For system i have selected FP VAV with reheat, than for FP vav box, I took 50 % of Total CFM (Cooling) and multiply 50 % of CFM by 0.3 to get wattage. And input total wattage into secondary supply fan in Fan tab. After reading above comment it sounds like, it is more complicated than what i did. Any suggestion? Thank you

Wed, 05/22/2013 - 14:54

Just to be clear the value is 0.35 W/cfm. We are not aware of any limitations in Trace for accurately modeling this issue. Anil's approach sounds right to us but we are not Trace experts. Consult the help desk again or post your issue on the Trace users group at onebuilding.org. Any other thoughts?

Wed, 05/22/2013 - 14:58

thanks Marcus and Anil that's easy way of doing it.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.