FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Using Desiccant Dehumidification - What about the Baseline?

In some cases, such as Hospital operating rooms and Ice Rinks, you have to maintain indoor air dewpoint temperaturs lower than 44 F. To accomplish this, you typically have to use either a desiccant dehumidifier or a low-temp, glycol chiller, neither of which have a very high COP. However, Appendix G seems to only allow for the use of a 6.1 COP chiller supplying 44 F water to provide all cooling and dehumidification in the Baseline. Not only is it this physically impossible for the Baseline chiller to do, but if you allow the energy model to disregard the laws of physics, this tends to create a larger disadvantage for the Proposed design to overcome. So is there a more equitable way to have the Baseline provide dehumidification when the Proposed design must use something other than a traditional chiller?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/08/2014 - 16:37

Check to see if any of the exceptions under G3.1.1 apply. Other quick thought would be to treat this as process perhaps?