A building provides outside air for ventilation based on CO2 concentrations in the return air. When CO2 concentrations exceed ambient + 590 ppm, the OA damper is opened to allow more OA to mix with return and reduce CO2 levels in the space. Fans speeds are also increased for OA AHU, floor AHU and return/relief. This essentially allows the building to operate with a lower amount of OA than the ASHRAE 62.1-2007 calculation requires. This “lower minimum” would essentially be the OA rate required based on the area OA rate (i.e., 0.06 cfm/sf) and distribution effectiveness, the people OA rate would be zero. In operation, as the building increases in occupancy, the CO2 concentrations increase, and OA rates are then increased to meet “demand” as measured by CO2 concentration. OA rate is increased until the CO2 concentration reaches acceptable levels (ambient + 590 ppm). As CO2 concentration drops, the OA damper is closed back down and fan speeds reduced to conserve energy.
The reference guide (O&M) even states that costs can be mitigated with CO2 monitors and demand control ventilation. However, there is no “Case 3” that lays out the requirements for how to operate and document the system as such.
Has anyone been able to use DCV to achieve this Prereq?
I'm thinking about writing up a CIR and submitting…
ASIDE: Wouldn’t it be nice if there was a place we could share “Project CIRs”? I wonder if LEEDuser would consider adding a feature for that…share the knowledge!