We have fixtures that are located in a covered area (under a plaza) which exceed the allowable uplight rating. It seems reasonable to exclude these fixtures from the uplight requirements since they are covered, but there isn’t any clear guidance on this issue. Any feedback would be most helpful.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Donald Green
Sr Project Manager / Operations ManagerProgressive AE
35 thumbs up
October 23, 2017 - 4:45 pm
Carlie - did you ever find resolution on this issue, dealing with it on a project now. Thanks!
Bill Swanson
Sr. Electrical EngineerIntegrated Design Solutions
LEEDuser Expert
731 thumbs up
October 23, 2017 - 4:52 pm
A lot of the responses didn't transfer over yet with the new website.
Any solid structure that blocks uplight can be considered as a shield. Draw a section of this area showing what percentage of the uplight is blocked.
Vegetation doesn't count as a shield.