FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Unconditioned vs conditioned space

Hello everyone, I know this topic has been addressed in several threads below, but I just want to try to have a better understanding of the subject. A conditioned space would be a space with a cooling or heating system installed, and ASHRAE 90.1 defines the minimum cooling or heating capacity that the system must have to be considered conditioned. I have a project with no air conditioning designed nor required, and the owner is completely positive that it won't be installed in the future. The reviewer suggests that the project must be modeled with cooling and heating, even if it does not exists (as stated in ASHRAE for conditioned spaces); and if I do this, the energy savings percent drops considerably. The equipment capacity estimated in the energy model does exceed the 5 btu/h/sf, so under ASHRAE, it would be considered a cooled space. How can I explain that this is an unconditioned space? Do I have to somehow prove that the space is comfortable without HVAC? It does comply with ASHRAE 62.1 with natural ventilation.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/04/2015 - 21:27

If it has no heating or cooling system it is an unconditioned space. Does it have a heating system? If not it is unconditioned. If it does you can model the Baseline as a system 9 or 10 according to Addendum dn. Since you have already done the model, you can also adjust the cooling temperature set points so high that the system never operates. As long as the set points are the same in both models Appendix G allows this. You only have to prove comparable comfort if you are claiming any savings related to natural ventilation.

Thu, 06/04/2015 - 21:58

Thank you very much for your response. We do not have heating here in Costa Rica, so i'll definitely consider it to be unconditioned. I will adjust temperature set points in the baseline and proposed case. We did mentioned in the first review that there would not be any HVAC system installed but the reviewer insists in including it in the model. If we adjust set points, and there is 0 energy consumption in cooling, would it be the same if we just don't model the equipment? Is there any specific document that I should make reference in the response narrative?

Thu, 06/04/2015 - 22:20

If the space has no heating or cooling then it is unconditioned and the reviewer is wrong. It happens. You could send a project team inquiry through GBCI's web site to seek clarification pointing out the definition of an unconditioned space. The effect of the equipment running should be the same as no equipment, zero energy use. I would just tell the reviewer the set points and indicate they are identical. See Table G3.1-b.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.