Dear all,

We have a case of CI fitout, with VAVs in project scope but no AHUs in our scope. The client leased an office area which receives mixed air (fresh+return) from the central AHU within the base building, this AHU doesn't have FA monitor installed, so do we still able to comply with the prerequisite without having FA monitoring?

I've noticed the LEED V4 CI wording states that: 

"For variable air volume systems with an outdoor air intake in the project scope of work, provide a direct
outdoor airflow measurement device..."

Our case is a VAV and the outdoor air intake is out of scope.