FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

UFAD System: Underfloor plenum in baseline model?

The proposed design is an Underfloor Air Distribution (UFAD) system utilizing an underfloor supply plenum and overhead return plenum. I am setting up the baseline model for LEED submission. The proposed building stories and area put us into Baseline HVAC System Type 5 (Packaged VAV w/ Reheat). My question is whether or not to include the underfloor plenum in the baseline model to be consistent with the envelope areas exposed to the space in the proposed building, even though the baseline will use an overhead delivery system. We are referencing ASHRAE 90.1-2007. Table G3.1 notes that the total gross area of exterior walls shall be the same in proposed and baseline, but does not mention whether the same envelope area must be distributed equally to plenums vs. spaces between the proposed and baseline. We are modeling with Trane TRACE 700. I am able to create the underfloor plenum in the baseline rooms, but when the overhead baseline system type 5 is applied, I am unable to enter underfloor plenum heights and raised floor heat transfer coefficients on the systems tab. TRACE help says that if a room has an underfloor plenum but is not assigned to a system with a UFAD supply, the plenum will be modeled as dead air space. Then how does TRACE model heat transfer between the dead air space and the room if I was unable to tell it a heat transfer coefficient of the raised floor assembly? I have the software's tech support looking into this as well. But my guess is someone has modeled proposed UFAD vs. baseline overhead VAV before using TRACE, and I'm wondering how they might have handled it. Thanks for the help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/05/2015 - 14:17

The Baseline does not include an underfloor plenum. The Baseline will technically have a greater volume of conditioned space but I do not this this will make any significant difference in energy use. Both models should include the return air plenum. Can't help with the specific Trace issues. If you have not already done so you could post your specific Trace issue on the Trace Users listserve at onebuilding.org.

Fri, 06/05/2015 - 14:50

That's what we were thinking too, but just wanted some confirmation. The TRACE issue goes away once there is no baseline underfloor plenum. Thanks, Marcus.