FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

U-Value / F-Factor

Hi, I have calculated the U-Value of a Slab on Grade Floor to be 0.12 (metric) using 100mm insulation. The Leed reviewer wants to see the F-Factor equivalent in agreement with ASHRAE 90.1 2007 Table A6.3 however the min horizontal insulation is 300mm (within this table) and it does not quote R values above R-2.6. Therefore there is no real direct match from this table that I can pick. What would be the best way to respond in this case. Will a calculated U-Value not suffice ?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/18/2016 - 21:17

ASHRAE doesn't really allow other calculation methods for F-Factors. Since your 100mm thick insulation would adequate +/-Rsi-3.5, I suggest you use the F-Factor of Rsi 2.6 as there's not a major change in value for unheated slabs. What's the width of your insulation? Also, have a look at Figure 5-K in the 90.1 User's Manual to see if you have others options depending on your project specifics.

Fri, 08/19/2016 - 15:56

You can extrapolate from the tables or provide a similar calculation to the method used in the table. LEED does allow other than F-factor calculations because some of the modeling software does not model F-factor.