FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Type and Number of Boilers

In the building that I’m modelling there are two floors. On the ground floor the conditioned area is 3393m^2 and on the first floor it is 2689m^2. The baseline system shall be System 5 – Packaged rooftop VAV with reheat. G3.1.1 states “each floor shall be modelled with a separate HVAC system”. Therefore I have to model a hot water loop for the ground floor and a hot water loop for the first floor. G3.1.3.2 states “The baseline building design boiler plant shall be modelled (..) as having two equally sized boilers for plants serving more than 1400m^2”. Does it mean that I have to model two HW loops (one for the ground floor and one for the first floor) and in every loop two boilers in parallel (i.e. considering the whole building four boilers)? With Regards

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/02/2013 - 14:30

You only need an air side system per floor. You would model a central boiler plant with a single secondary loop serving each of the systems.

Fri, 08/02/2013 - 15:04

The surface is more than 1400 m^2. Shall I model two boilers, in parallel in the same HW loop (for the whole building one HW loop and two boilers)? On the demand side, I would connect the water coils in parallel.

Fri, 08/02/2013 - 15:52

Yep two equally sized boilers (G3.1.3.2) with a single primary HW loop (G3.1.3.5).