In the building that I’m modelling there are two floors. On the ground floor the conditioned area is 3393m^2 and on the first floor it is 2689m^2. The baseline system shall be System 5 – Packaged rooftop VAV with reheat. G3.1.1 states “each floor shall be modelled with a separate HVAC system”. Therefore I have to model a hot water loop for the ground floor and a hot water loop for the first floor. G3.1.3.2 states “The baseline building design boiler plant shall be modelled (..) as having two equally sized boilers for plants serving more than 1400m^2”. Does it mean that I have to model two HW loops (one for the ground floor and one for the first floor) and in every loop two boilers in parallel (i.e. considering the whole building four boilers)? With Regards