Forum discussion

Treatment of shared chiller plant

We have a central chiller plant generating chilled water to serve a hotel and a convention centre. Only the convention centre will be seeking LEED certification under LEED NC 2009. We have a couple of queries: 1. Is it compulsory to account for shared chiller plant and the associated change in part load efficiencies, increased pumping energy etc? It would be more conservative not to account for as part load efficiency would tend to be lower and pumping energy higher as the cooling load increases serving two buildings. 2. If it is compulsory do we need to follow the methodologies in the DESv2 doc or can we construct our own methodology? 3. Is the most recent version of the DESv2 doc the August 2013 publication? Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/25/2015 - 13:47

1. It depends on the methodology you choose. 2. You have three previously accepted options - DESv2 Option 1, DESv2 Option 2 or ASHRAE 90.1-2007 Addendum ai. Constructing your own methodology is acceptable but far riskier since there is a chance that your methodology may not be accepted. If you create your own I would suggest you get some level of approval through a LEED Interpretation. 3. DESv2 was published August 13, 2010. I am not familiar with an August 2013 version. Do you have a link to it?

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.