NC-2009 SSc6.2:Stormwater design - quality control

Treating stormwater only?

Could this credit be achieved if it were only proposed to treat the storm water runoff with a structural measure and not capture? It would also need to accommodate at least 90% of the annual rainfall volume AND remove 80% of the avg annual postdevelopment load of TSS? Is that correct? thanks, NK

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 02/28/2013 - 12:09

Like a CDS or other hydro-dynamic separator? Sure, as long as the appropriate runoff volume is treated at 80% TSS or above.