according to the picture you see on the books for pre-requisites, I want to know if there is any restriction of use of toilets and urinals with fluximeters, or just in all cases require only that do not exceed 1.6 gallons per discharge.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Carlie Bullock-Jones
PrincipalEcoworks Studio
LEEDuser Expert
220 thumbs up
September 5, 2012 - 6:18 pm
Hi Ronald,
There is no restriction on the use of flush meter valves used on water closets urinals. Note that the baseline for water closets is 1.6 gpf and for urinals is 1.0 gpf and you are correct that you cannot exceed these flush rates; however, to demonstrate compliance with the prerequisite (minimum 20% reduction over EPAct) you will likely need to consider lower flush rates on these fixtures.
Hope helpful!