Testing of Existing Old Roof Material

We would like to take a sample of 10 year old existing roofing and test it in a laboratory for the aged SRI value. It seems the ASTM E 1980 and CRRC-1 test methodology only deals with simulated aging. Is it acceptable to test existing truly aged materials?  

Thanks very much, 

Doug Snyder

Hanoi, Vietnam

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/03/2017 - 17:38

Mr. Snyder, We have successfully achieved this credit by doing exactly that - had a piece of a dolomite aggregate roof tested at a building in San Francisco, CA to determine the SRI and pushed this through the LEED review process with no issues. Be sure to inquire with the testing agency how large a piece of the material needs to be submitted, there is a minimum sample size, and I believe there must be more than one sample sent.

Thu, 10/26/2017 - 09:23

Dear Levi Jimenez, Thanks very much for your helpful reply. Best, Doug