Forum discussion

NC-v4 EAc1:Enhanced commissioning

Test and balance

I understand that there were not any requirements regarding TAB in LEED 2009 -- is this still true for v4?  Just want to confirm that there are no issues with having the balancer contracted under our construction manager.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/04/2021 - 18:50

LEED v4 does not have a contract language with respect to the balancing contractor and who they can/cannot be contracted through. 

Tue, 12/19/2023 - 21:10

Dave, Is there any language about the amount of TAB verification?  Like a percentage or something?

Tue, 12/19/2023 - 22:33

LEED does not go into that level of detail in regards to balancing.....but remembering back in my HVAC design days a long time ago, I never recall a project that 'sampled' the test and balancing. Every system level (e.g. air handling units) every zone level (e.g. variable air volume boxes) and every diffuser/fan/pump were included in the balancing.  Commissioning tends to sample 10% to 20% of all zone level equipment while commissioning all system level equipment. Commissioning Authority will probably spot check airflows at some of the diffusers/grilles.