Forum discussion

CS-2009 EAc1:Optimize energy performance

tenant work: fan coils

Hello all, I'm working on a C&S project. The whole building is already leased to one client, who wants to use one half as laboratories and the other as offices. For the ventilation of the laboratories a 100% OA-system is part of the C&S-development, with the ducts ending right in the shaft. The office spaces are ventilated naturally. Chillers are installed on the roof (as part of C&S) and cw-pipes are installed, ending right in the shaft, too. These can be connected to fancoils, working only with recirculation air, but this is part of the tenants work (and most likely to be done as we are planning with cooling loads > 100 W/m² in the laboratories). There are no agreements with the tenant facing this. The Baseline is simulated with System 5. In my understanding, equipment, that is not part of C&S should be modeled the same in Proposed and BL. But having a 100% OA system on the one hand and System 5 on the other, I really don't know how this equipment should be modeled. I thought of adding Fancoils in both systems, sized equally, that make up the recirculation air. But then I fear frictions in the autosizing of the Baseline. Would be glad to get your opinions.

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/19/2012 - 16:50

Equipment not part of the CS can be included if it has already been designed or installed. You would only need to model the Proposed and Baseline identical if there is no tenant space design/installation. If you have a completed tenant space design you can model it as designed/installed and claim credit for any savings. Several of the addenda that became a part of ASHRAE 90.1-2007 were specific to accounting for lab spaces so a fair comparison can be made.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.