Forum discussion

CS-2009 EAc1:Optimize energy performance

Tenant Area HVAC System

Hi, I am working on a mixed use project with retail on 1st floor and office on 2nd and 3rd floor with a total project area of 115,000 sf. The core spaces are designed to be served by water source heat pump system (Boiler and fluid cooler combination) with 100 % outside air heat recovery ventilators (HRV). The plant side (Boilers and fluid coolers) as well as the HRV (with OA and SA requirements determined) are sized and designed for meeting the load requirements for both the core and tenant spaces. With the plant side and outside air system defined adequately it is project teams intent that tenants will install there individual WSHP system, however it is not included in the tenant lease agreement. In this scenario, can we include the WSHP for the tenant spaces in proposed design model and claim savings associated with them or we are still required to model the tenants space HVAC system same as baseline system? Thank you in advance for advice.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 07/11/2013 - 14:54

If the system is designed or if the system parameters are spelled out in the lease agreements you can model the proposed case with the chosen system. If neither is in place then you are required to model the baseline system in those spaces.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.