FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Task lights in college dorm

Is this correct: If students bring their own task lights (and we don't know what they'd bring) we do not include them in our lighting power density calculation? We have fixed overhead lighting.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/28/2015 - 14:51

You do need to include an allowance for task lighting in your lighting power density calculation. The only lighting you do not count in that calculation are the exceptions to Section 9.2.2.3. Dorm task lighting is not an exception. An exception would still need to be modeled identically as process lighting. Some universities have a policy about the type and wattage of task lighting allowed in dorms. My daughter's school only allows CFLs or LEDs. You may be able to use this to determine the wattage to include if such a policy exists at this school, otherwise you will need to make an assumption and be able to defend it.

Thu, 05/28/2015 - 15:01

Makes sense. Otherwise you'd kind of be penalizing projects that spend the money to provide task lights ...

Thu, 05/28/2015 - 15:46

It's a good policy. I say only allow 6 watt (or less) LEDs- that's what I have on my desk and it's easy to put these bulbs in any old fixture with an edison screw. The 13 watt CFLs were good but it is a pain when they break and you have mercury to dispose.