FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Taking credit for DCV in car parks

Hello Marcus Sheffer, Refering to the LEED Interpretation 10371 related to taking credit for DCV in car parks, it is specified: 1) that the proposed case should be modeled such as that a minimum air flow of 0,05 cfm/ft2 should be maintained; 2) that car park ventilation rate and fan power in the baseline building shall be modeled as 0,75 cfm/ft2 and 0,3 W/cfm, respectively. Can you please tell me the source of the following numbers: a) 0,05 cfm/ft2 as minimum exhaust rates for the proposed building; b) 0,3 W/cfm for the fanpower in the baseline building Thank you in advance, Best regards, Pedro Ribeiro

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/16/2016 - 16:46

a. We think the 0.05 comes from the International Mechanical Code 2009 minimum Section 404.2. b. The 0.3 probably comes from the fan power requirements for system 9/10 in 90.1-2010 but we are not sure.

Thu, 08/18/2016 - 14:32

Thank you for your response, Marcus! I still have a few questions regarding this matter: a) Can I claim savings with the DCV for car parks ventilation, even though there is a portuguese law (where the project is located) that requires this DCV? (meaning that this is standard practice); b) If not, and since this DCV is standard practice, how do I model the Baseline case? As per ASHRAE 90.1 - 2010? Or as designed? c) If it is as designed, am I right to assume this as process load, since it is not regulated under ASHRAE 90.1 - 2007?

Fri, 08/19/2016 - 16:05

a. No. If it required by local code then that is the baseline in that area. b. Identical to the design. c. Yes it is a process load