FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Take credit for variable temperature setpoints in hotel rooms

We have a hotel project where heating setpoints in hotel guest rooms are 21 degrees Celsius when the room is occupied and lowered to 18 degrees Celsius when the guests are not in the room. This is controlled by the keycard-holder in the entrance to the room (which also controls the lighting). Are we allowed to model this in the Proposed energy model, and should the Baseline also be modeled with this control or are we allowed to take credit for this energy efficiency measure?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/17/2015 - 09:28

You are allowed to model it. The setpoint schedules must be the same. Ramping setpoints up and down sometimes uses more energy rather than less in some cases. I would not recommend it for radiant hydronic systems, for example, but for a hotel fan-coil, you're probably okay.

Wed, 06/17/2015 - 19:43

See one of the appendices in the Advanced Energy Modeling Guide for LEED for an example.

Thu, 06/18/2015 - 12:36

Ok, many thanks!