FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Table 6.8.1D - System 2

We are simulating a hotel building with System 2 PTHP. However, when it comes to table 6.8.1D for the minimum efficiency requirements, it is unclear what is meant by the formula 3.60-(0.213XCap/1000)c COP. Is Cap related to the capacity of the real product used in the proposed building or the value that comes out for cooling capacity at the baseline output?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/21/2016 - 14:55

This is both the minimum mandatory standard COP for your projects PTHPs, for this size and the formula you need to use to calculate COP for your baseline model. To calculate minimum mandatory COP: 1. Get PTHP capacity (in kW). 2. Calculate minimum COP = 3.60 - (0.213XCapacity/1000) 3. Check for note c in the bottom of the table to see if it applies. To calculate COP for the baseline: 1.Do a sizing run 2.Get the design capcacity (in kW). 3.Calculate COP = 3.60 - (0.213XCapacity/1000) 4. Check the note at the bottom of the table to see if it applies: c Cap means the rated cooling capacity of the product in kW. If the unit’s capacity is less than 2.1 kW, use 2.1 kW in the calculation. If the unit’s capacity is greater than 4.4 kW, use 4.4 kW in the calculation.

Thu, 09/22/2016 - 06:37

Thanks Santiago!

Fri, 09/23/2016 - 14:14

Make sure to apply the Baseline system over-sizing factor in G3.1.2.2 when you have done your sizing run.

Thu, 12/21/2017 - 11:11

Is the rated cooling capacity Cap the cooling capacity of the cooling coil - the heat provided by the fan? - is minus Or simply the cooling capacity of the cooling coil?

Thu, 12/21/2017 - 14:37

As for the heating coil minimum efficiency for System 1, I see PTAC (cooling mode) only. Where can I find the limit for heating mode? SORRY, I SEE THAT THERE IS A "HOT-WATER FOSSIL FUEL BOILER", THEREFORE I HAVE TO CONSIDER THE EFFICIENCY FOR BOILERS.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.