FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Table 1.4.7B - Proposed Air-Side HVAC System Schedule - Outdoor Airflow cfm

Hi,

I need a couple of clarificaitons regarding the Outdoor Airflow that has to be listed in Table 1.4.7.B of the proposed systems. The project is located in California.

The helpful notes(grey column) mention "Actual minimum outdoor airflow rates consistent with Mechanical Schedule". 

a) Is this an indicator that it should at least provide the minimum OA per the schedules; or must the cfm match the minimum OA cfm of the system?

b) In our project, the mech schedules a range of OA with min and max. If the answer to question (a) is yes, then in the case with the min/max range, is it acceptable if the inputs for Table 1.4.7B are within the range; or must they also match the min OA?

Thank you,

Maria

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/05/2017 - 15:31

The maximum OA is the cfm that should be entered for the Proposed systems. The model is required to reflect the actual design of the systems. So the summary of the modeling inputs should be the same as the values in the mechanical schedules. If something changes to make the schedules inaccurate then the discrepancy should be explained.

Thu, 10/05/2017 - 16:35

Hi Markus, Thank you for your response and clarification. If it's the maximum to be entered why does the grey Help column says minimum? That causes confusion. Regards, Maria

Wed, 10/25/2017 - 19:58

The grey box advice is assuming that any maximum would be related to economizer not demand controlled ventilation. Sorry it took so long to get back to you I had to ask the author of the spreadsheet.