FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Table 1.4.7B Entering Outdoor Airflow in Baseline

Greetings, There is a clarification issue while entering these values in the Baseline about which I'd appreciate some advice. The OA flow should be identical in both models. When calculating the HVAC systems in Baseline (system 5 or 7), and since these are multiple-zone systems, the OA is corrected at the end by Ev and with exception of Ev=1 the OA which is calculated (corrected Vot) is bigger. In Propose case however almost always the Ev is different, in most of the cases bigger than the Baseline one. The question is: should I enter the uncorrected OA flow in both cases, in order in the table these values to appear equal, besides this way it will reflect exactly the project design. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/09/2014 - 19:49

The Proposed should be based on the design value and the Baseline should be the same in all areas without DCV.

Tue, 12/09/2014 - 20:02

Thanks for the reply. However it's kind of unclear to me the comment about DCV. As I've tried to say, the only way the OA to appear identical in both Proposed and in the Baseline is to enter the uncorrected OA value in accordance to ASHRAE 62.1 terminology. The question was am I right in such suggesting. Thanks.

Wed, 12/10/2014 - 15:02

No DCV - model OA identical based on the actual equipment designed/installed. If the equipment is designed with 1,000 cfm of OA then that is what gets modeled. With DCV - again model the proposed based on the actual equipment designed/installed. The baseline OA is modeled using the ASHARE 62 calculation for the proposed and this should be the same as the Vot calculated for IEQp1.

Thu, 12/25/2014 - 12:56

Hi Markus, thanks a lot for your replies. However there are some final clarifications on this issue I'd like to ask about. So, the number of people and the ventilation rates (as per ASHRAE 62.1) are entered absolutely identical in Proposed and Baseline model. The OA when it is 100% is also identical. The Voz (ventilation outdoor air per zone) are identical too. When it comes to compare the Vot values, the quantities are not identical with the exception of 100%OA. For the Proposed I can enter the Vot from the IEQp1 form, but for the baseline I'm taking it from the calculation reports of the energy simulation software. I assume that this difference in Vot values is due to the systems with DCV. The Baseline systems are one per every floor, whereas the Proposed ones are arranged differently and probably because of this the totals are different. The Question is: It in Table 1.4.7 in the row of Outdoor Airflow, if the Vot values are entered and the totals appeared not identical, should this be a problem or be questioned for explanation by the reviewer. Thanks.

Fri, 12/26/2014 - 20:15

The difference between Vot and Voz is usually due to systems with DCV in the proposed case. If there is a difference reported in the 1.4.7 tables and there is DCV in the proposed the reviewer will expect to see that the baseline OA is slightly less than the proposed OA. Also keep in mind that the OA being identical is in cfm quantity not based on percentage. A 100% OA system in the proposed may not be 100% OA in the baseline depending on the auto-sized supply cfm in the baseline system. In systems without DCV the proposed OA is modeled as designed (not using the Vot). The baseline systems are identical. In systems with DCV the proposed OA is also modeled as designed but the baseline uses the Vot value.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.