FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Table 1.4.7A - Baseline Air-Side HVAC System Schedule

Greetings, The issue I'd request for advice and support is related to some reviewer's remarks. 1. It is for Supply Airflow. The baseline system is 5. The calculation reports about design air flow quantities for the Baseline show two different quantities - one for Cooling airflow and the other for Heating airflow. Which one is to be entered in the table? 2. It is for Outdoor airflow (in the same table). Within the Outdoor air systems there are systems which are using outdoor air, but just for pure ventilation purposes - like transformer room, sprinkler room, etc. Should such air be entered in this line (Outdoor Airflow?) Your advice would be highly appreciated. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/06/2014 - 21:59

1. If they are not the same enter the higher of the two. 2. This line is for the outdoor air you bring into a space. If it is exhaust air only is does not get entered as outdoor air.

Fri, 11/07/2014 - 06:37

Re: 2. Where does the makeup air come from? Outdoors directly (unconditioned) or from other conditioned spaces (i.e. from outdoors via an AHU and other zone conditioning equipment, conditioned)? What is the fresh air requirement of the space (transformer room)? Lastly, if the loads of the space differ significantly to the other spaces (as is likely for the transformer room), then it should be on a seperate system as per the exception. Right? And then set the "needs" for heating cooling and ODA as they are for a transformer room, i.e. If it is conditioned then Heating Setpoint 5C, Cooling Setpoint 32C, ODA requirement in the proposed = 0. If it is not conditioned then you could handle the exhaust as a process load.

Fri, 11/07/2014 - 08:55

Thanks a lot for the reply. There is however one more clarifying question to this issue. It is for the ventilation systems which are purely exhaust systems - like garage, transformer room and for which the intake is compensated by open doors/grills to the outside. As in table 1.4.7 there is not a separated line for the exhaust air, the only place left is Exhaust Fan Power line. Is this the only place where the fan power of this system is to be entered (without indicating their airflow quantities? Thanks.

Fri, 11/07/2014 - 14:42

If it is a regulated exhaust fan (part of a system) then it gets entered in the 1.4.7 tables. If it is process then it gets entered in table 1.4.4.

Fri, 11/07/2014 - 14:56

Thanks for the reply. If I rephrase the question as: If the ventilation system consists of an exhaust fan only (garage, transformer room) and nothing else, does it mean that I should enter it in 1.4.4. Such fans are also regulated - they follow some control - either by CO2 or by some schedule ( if I enterpred the word "regulated" properly). Thanks.

Fri, 11/07/2014 - 15:01

Those are process load fans and are entered in 1.4.4. Regulated does not mean controlled. Regulated means that 90.1 contains a mandatory or prescriptive requirement for the item in question. 90.1 does not have any requirements that would establish a baseline for these exhaust fans so they are considered a process load.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.