FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

System Type 9 Baseline Fan Sizing

I am working on a job with the Army Corps of Engineers that has a vehicle maintenance workbay with general exhaust requirements of 1.5 CFM/SF dictated by the RFP. We are to provide makeup air to maintain a slight negative pressure in the space via a hot water make up air unit. The airflow rate in the proposed case is being dictated by the exhaust requirements in the RFP. Appendix G states that the baseline fan sizing for System Type 9 shall be based on the required air with a 105 discharge air temp, minimum outside air, or "as required to comply with applicable codes or accreditation standards." My question is can I model the airflow identically in the proposed and baseline cases as the airflow is dictated by the RFP (could this be considered an accreditation standard as the Army Corps of Engineers are dictating this design criteria?) Any help would be greatly appreciated!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/02/2017 - 13:48

The quantity of outdoor air is always modeled identically in both based on the proposed design (unless there is DCV in the proposed). The proposed would be modeled as designed and the baseline according to Appendix G. The exhaust fans sound like they are part of the system so they are basically already included in the baseline fan power allowance of 0.3 W/cfm and should not be added separately.

Add new comment