FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

System designation

Hi everyone

We have this project that consists in Hotel and retail spaces, where the retail spaces are owned by the hotel but leased to third party. 

We are kind of lost selecting the correct baseline system, we are aware that hotel shall be System 2 PTHP. But for the leased areas:

1. Should we consider System 6? (more than 25000sqft) Since its not residential/hotel per se. Or,

2. Should we consider all hotel zones (regardless if owned by self or leased) as system 2?

 

Another little "inconvenient" is, since we are talking about a really big project, model software was somewhat unable tu run the complete model, so we split it into 2 different energy models. We are obviously going to submit all corresponding documentation (1.4 table, energy reports) for both models, but could this be subject to be flagged during the review?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/18/2019 - 22:41

It could be separate - even though it is owned by the hotel, the use and schedule of it will be different than the rest of the facility. You may see the hotel design case also have separate systems for the retail section. What software program are you using? Many programs allow the use of "multipliers" in case you have some typical zones that could be modeled once and multiplied in case this helps you. You may also be able to combine some zones that are equivalent (90.1 includes some guidance on what can be combined) if you are hitting a limit on number of zones. Splitting the model may cause some inaccuracies for fan systems that serve the whole building, or if the design case uses central heat or cooling.      

Mon, 02/18/2019 - 23:27

Actually I considered maybe making all system 2 and just use different schedules for hotel/retail section. Mostly because, at least in proposed, they do have the same central cooling equipment. Could this be the most effective way? The HVAC System is fan and coil units connected to water cooled chillers, and chillers connected to their respective cooling tower. Fan and coil units are provided by the hotel in owned areas such as: Service zones (administrative offices, guest amenities, and conference rooms) Guest units Retail main corridor. (Retail locals are being provided with chilled water piping terminals and tenant will be instructed via TSLA what kind of units they might install). Spliting it may indeed cause some inaccuracies mostly in chiller performance. Since I was thinking modeling the exact same system but assigning the gpm's according to corresponding zones. Knowing that this is not as accurate as I would like to. I'm using eQuest, and yes, I already multiplied the 20x storys and combined guest units un 4 sections according orientation. The thing here is, project features plenum spaces and eQuest makes 1 plenum per zone, so basically the "double" zones are crashing it. Project is simply too big and complex. Thought it would be accepted claiming "software limitation" since it is unpractical to have one model. 

Tue, 02/19/2019 - 14:58

You are required to apply any of the exceptions to G3.1.1 if they apply. If the non-residential is over 20 k sf then (a) applies. If not then you technically should model a system #2 everywhere. You will definitely need a very thorough justification for combining two separate models. You can do so only if you can justify that doing so will produce a conservative result.