Greetings,
The question is related to modeling rooms/zones which are to be assigned to System 9.
In the Proposed, these rooms/zones are having supply, return and sometime room exhaust ventilation.
When however a System 9 is to be modeled, the App. G mention the fan power related only to the supply air flow.
What should be used for Return/Exhaust fan power for System 9.
Your advice will be highly appreciated.
Thanks
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5914 thumbs up
July 4, 2017 - 12:54 pm
The baseline fan power allowance includes all of the system fans. You can allocate the kW a number of different ways depending on the systems.
Vassil Vassilev
ManagerTermoservice
13 thumbs up
July 5, 2017 - 2:41 am
Hi Marcus,
Thanks for the reply.
The fan power for System 9 is clear - CFM x 0.3 - over.
How about fan power adjustment for this system?
In the Proposed there are filters and sound attenuators. How to add their static to the System 9's fan power. Without this the comparison is favorable for the Baseline and it shouldn't be so.
Your opinion and advice are highly appreciated.
Thanks.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5914 thumbs up
July 5, 2017 - 12:30 pm
There are no pressure drop adjustments for System 9 or 10.
These systems only apply to certain space types such as storage rooms, stairwells, vestibules, electrical/mechanical rooms, and restrooms not exhausting or transferring air from mechanically cooled thermal zones in the proposed design. You cannot use these systems except for those space types. LEED allows them to apply to warehouses which I guess is just a large storage room.
Vassil Vassilev
ManagerTermoservice
13 thumbs up
July 13, 2017 - 5:35 am
Hi Marcus,
Thanks for the reply.
Practically, for system 9 what value for Static pressure is to be entered in the modeling software.
Thanks.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5914 thumbs up
July 14, 2017 - 12:36 pm
Appendix G does not indicate a static pressure setting so it should be identical to the Proposed.