FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

System 7: selection of heating system

I,m working on a project were the proposed building has 2 ground water heat pumps with total capaciyt approx. 2300 kW. According to ASHRAE G3.1.1 should I select the system 7, fossil fuel boiler for the baseline and in table 6.8.1 there is a equivalent heat pump. Should I really select fossil fuel boiler for the base line or select an equivalent ground water heat pump? thank you for your help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 11/06/2013 - 14:36

If you have electric heat you would select a baseline system from the electric column in Table G3.1.1A. This would result in a system 8 assuming the same building area and # of floors.

Wed, 11/06/2013 - 15:54

but the heating system is convered by heat pump 50% and district heating 50%. Should I calculate energy save differentlly for the fraction of from heat pump and from district heating?

Wed, 11/06/2013 - 16:23

If it is a hybrid system then a system 7 is right.