FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

System 2 - LEED Fan Power ASHRAE 90.1.2007

Hi, Greetings! I am doing Energy Model for Labor Accommodation. I have some doubts and need your help, Baseline system will be system 2 as per ASHRAE 90.1.2007. Since, the project is matching with residential category. For Baseline Model, Fan power requirement is 0.3 W/cfm. Further, Our software needs the following inputs for fan power. 1. Power (i.e. fan power) 2. Temperature Rise 3. Motor Efficiency Whether this 0.3w/cfm is including efficiency of the motor or without efficiency. How to calculate temperature Rise & efficiency manually & do u have any spreadsheet. Please Thanks......

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/13/2017 - 13:50

See G3.1.2.9, there is no motor efficiency in the calculation. Not sure what you mean by temperature rise. G3.1.2.8 covers the delta T required if that is what you are looking for. There is a fan power calculator in the documentation toolkit above.

Thu, 04/13/2017 - 15:48

I think he is referring to the heat rise across the fan not the delta T for airflow sizing. Most software will calculate the heat rise based on the power and efficiencies.

Thu, 04/13/2017 - 16:10

ignore