FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Suspended Ceiling

Dear all, I have a suspended ceiling with a 60 cm air gap between the panels and the reinforced concrete slab where all the electro-mechanical lies, but it doesn't act as plenum zone since that all return, supply, and exhaust are ducted. Now this zone where all electro-mechanical lies is an unconditioned zone with assumed temperature of 80F. As for the basecase simulation, I've set the concrete floor assembly U-value as per ASHRAE 90.1, but what about the Basecase for the gypsum-board separating conditioned zones from this false ceiling zone? can I use gypsum U-value from the eQuest library?, or should I model it same as developed case (actual design) where a 5 cm layer of insulation is placed over these panels? and in that case I won't gain any credit from this insulation layer. Another question is that these zones are covered by veiling glass with insulation layer on all facades, so in basecase; should it have the same U-value as exterior wall since that it is opaque (veiled) glass area?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/14/2014 - 18:17

Your assumption that this is an unconditioned zone is not correct. This is part of the conditioned space. Even an insulated drop ceiling is considered to have no insulating value within 90.1. Take away your operative assumption and I assume that the remaining questions become moot. Sounds like you are referring to what we call spandrel panels. If they are opaque then they are considered walls, so yes.