NC-2009 IEQc1:Outdoor Air Delivery Monitoring

Special Circumstance - Ventilation Air Not Required

We have a building with a large area of lockers/toilets. According to ASHRAE 62.1 these spaces do not require ventilation air. These spaces do require exhaust air. Due to the large area of these spaces and minimal conditioning requirements, these spaces are being served by a dedicated 100% OA unit that heats and/or ventilates only. Since these spaces are not required by ASHRAE 62.1 to be provided ventilation air, do these units need air flow monitoring? (The rest of the facility will have airflow monitoring as required). Yes, these serve non-densely occupied spaces only. If yes, CT's on the fans meet the requirements per CIR ID #2099, right?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/07/2014 - 18:04

If it is only for make-up air for the required exhaust, then it is not required.