Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

spaces,zones and systems in the energy model

do the spaces,zones and air systems in the baseline should have the same names as in the proposed design and the ones in the upploaded drawings? in the mechanical equipments schedules the engineer changed the name of the system to combine same capacities what shall i do in the energy model. regards

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 06/04/2012 - 16:03

Not necessarily. Sometime the total number of systems is different (see G3.1.1) and the type of system is different. Model the mechanical equipment as designed. If combined on the schedule you should still model the appropriate zone or thermal block associated with each piece of equipment.

Mon, 06/04/2012 - 16:33

Marcus, So you mean if I am using equest, i have to enter the equipments capacities ( in detailed mode )as shown in the equipments schedule and not let the software calculate it?

Mon, 06/04/2012 - 17:01

Yes you do. The Proposed model should have almost nothing auto-calculated.