Dear community,
I have a project where some spaces will be left for future use, while most of others are designed and built for immediate use. I am wondering if I must include them as conditionned or unconditioned zone.
Many thanks,
Forum discussion
NC-2009 EAp2: Minimum Energy Performance
Dear community,
I have a project where some spaces will be left for future use, while most of others are designed and built for immediate use. I am wondering if I must include them as conditionned or unconditioned zone.
Many thanks,
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
A portion of our building envelope is historic. Can we exclude it from our model?
For an existing building, do I need to rotate the model?
Our process load is higher than 25%. Do we have to justify that?
Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?
Can mezzanines open to floors below be excluded from the energy model?
How do I provide a zip code for an international location?
For a project outside the U.S., how do I determine the climate zone?
For a project outside the U.S., how do I determine the Target Finder score?
Do hotel rooms need automatic light shut-off control?
How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?
The Section 9 space-by-space method does not include residential space types. What should I use?
Can the Passive House Planning Package (PHPP) be used to energy model for LEED?
Which baseline HVAC system do I use if my building has no heating or air conditioning?
Our project has a diesel backup generator. Should we include it in our energy model?
Can SHGC be higher in the proposed than in the baseline model?
Kristina Bach
VP of InnovationSustainable Investment Group
151 thumbs up
April 3, 2014 - 1:18 pm
You will want to review LEED Interpretation 10102 in detail (assuming it was posted before your project was registered). There are a variety of additional requirements for LEED-NC projects which include incomplete spaces like you describe.
For EAp2/EAc1, my understanding is that the energy model should be simulate those spaces as fully fit-out with the fit-out being identical in both the baseline and proposed cases (i.e. you can't claim any savings in those future spaces). This essentially means that the rest of the building/areas you fit-out now will need to be just a little more efficient to help carry the unknown/potential energy use of the incomplete spaces.
Valentin Grimaud
Thermal EngineerTERAO Green Building Engineering
43 thumbs up
April 4, 2014 - 6:02 am
Thank you very much.
That is my interpretation of table G3.1, too. Those spaces may be simulated fully fit-out as office spaces by default.