How are Open Plan Office areas classified in terms of the Sound Transmission section?

I am trying to determine what composite STC/NIC to design for at areas that are adjacent to Open Plan Office areas (with "cubicle" type workstations).

 

For example:

If you classify Open Plan Offices as "Collaborative / multi-use" the requirement is STC-45 at adjacency with "Private" offices. If you classify Open Plan Offices as "Hallway, stairway" the requirement is STC-35 at adjacency with "Private" offices. 

 

Which of the above is correct? Or is it none of the above?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/17/2019 - 21:35

Hi Tyler - I recently asked this exact question to the GBCI and got the following response:  "For an open office adjacent to a enclosed office (presumably private office) next to it, the adjacency combination of "Collaborative / multi-use" and "Private" would apply." Hope this helps.