Forum discussion

NC-2009 IEQp2:Environmental Tobacco Smoke (ETS) control

Smoking Room, Smoking Cabin

Dear all, I have a question regarding the use of smoking cabins in a LEED project, has anyone ever tried to install one or is willing to share their experience? Would the requirement be met if the cabin can provide the negative pressure difference of 5 Pa? There is an example diagram on page 419 of the BD+C V3 reference guide, where there is an Ante-Room for the smoking room, would this requirement also be necessary given the cabin is a stand alone unit? Thanks!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/24/2016 - 02:57

Hola! The ante-rooms are not required, but may be good practice. It is OK to use the cabin as long as it can keep the minimum negative pressure and exhaust directly to the outdoors 25 feet away of any openings.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.