Our MEP sub-contractor need to clarify if we can use an smoke capsule for duct leakage test? prior to air leakage test since the project specs is giving a small allowable 1% from basis of design?
if yes, is there any precautions?
Forum discussion
NC-2009 EAc3: Enhanced Commissioning
Our MEP sub-contractor need to clarify if we can use an smoke capsule for duct leakage test? prior to air leakage test since the project specs is giving a small allowable 1% from basis of design?
if yes, is there any precautions?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
February 23, 2017 - 11:09 am
First of all, it depends on your specifications. What test was required? Typically I would require something that comes from the SMACNA standards. If your project only gives the requirement of 1% (which is indeed tight), then the contractor has to propose more than just a method, they have to show how that method will demonstrate the standard. Personally, I do not feel smoke is a good test other than it sounds good. How do you quantify smoke? There is a standard test which involves sealing the ductwork system outlets and then pressurizing the ductwork to the operating conditions (perhaps 4" if a VAV system) with a characterized fan that allows precise measurement of airflow. Then this flow is compared to the maximum system airflow to gain a percentage. Seek guidance from a qualified testing and balancing agent...they know the right way to do this test.
Abdulla Anwar
Lead Design Architect | LEED Professional coordinatorNesma & Partners
February 25, 2017 - 4:25 am
Thanks,
as per project specs, The subcontractor will do the pressurized test.
he needs to confirm specimen on the ground before installation, his concern if that smoke gas might be contaminate the air entire ducts for IAQ on later stage? thanks in advance for advise.
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
February 27, 2017 - 4:11 pm
Ok, not sure that I understand how they would do that, but I would not recommend smoke. Most "cold smoke" machines use some kind of oil or other material that looks like smoke but is cold and should not irritate lungs unless way too much is used. It does not act like smoke in a fire and I would have a hard time seeing that it would do what the contractor is hoping for. If they are testing the longitudinal seams on the ground, I could see creating some kind of appliance that blanks off both ends and then allows application of low level compressed air. Too much and you would damage the seam, too little and it would not be a good test.
If they persist, I would ask for more information on how they are making the smoke and what the material is and how it might affect other credits.