In Table 5.3 point 5 of annex G of ASHRAE 90.1-2007 I find that for the baseline building performance “opaque assemblies used for new buildings (..) shall confirm with the following common lightweight assembly maximum U-factors in Tables 5.5-1 through 5.5-8:
(..)
- slab-on-grade floors shall match the F-factor for unheated slabs from the same tables.”.
Given a building, how can I calculated the F-factor of its slab-on-grade floor?
The technical standard EN ISO 13370:2008 considers the U-factor of the slab-on-grade floor as the thermal resistance between the internal surface of the floor and the external air, passing through the ground.
“To allow for the three-dimensional nature of heat flow within the ground, the formulae in this International Standard are expressed in terms of the “characteristic dimension” of the floor, B', defined as the area of the floor divided by half the perimeter” (see. Par. 8 of EN ISO 13370:2008).
Does ASHRAE use the same approach as EN ISO 13370:2008? How have I to calculate U-factor and F-factor for slab-on-grade floors, according to annex G of ASHRAE? Can I find documentation concerning this issue, please?