FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Slab on Grade F-factor for a large building

I asked this a couple of days ago on the HAP users forum and no one has responded so hopefully I'll have better luck here. I am working on a very large church complex (45,000 sqft) with about 80 spaces. The architect intends to use 24" of R-10 insulation in the vertical plane which should be an F-factor of 0.54 for the proposed building. According to Table 5.5-5 in 90.1-2007, the base building needs an F-factor of 0.73 and no insulation is required since the floor is unheated and it's a non-residential space. I don't have a good handle on how to properly represent the F-factor in Carrier's HAP since it only allows a slab U-value, edge insulation R-value and exposed perimeter length. Has anyone determined a good way to do this? And do I need to calculate a different U-value/insulation combination for each space? It seems to me all of the spaces are going to have the same slab and edge insulation, so they should all have the same inputs other than their exposed perimeter.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/29/2011 - 16:24

Hi- I don't normally use F-factors, as I use Carrier HAP to calculate loads. I agree that the spaces should all have the same inputs (floor U and edge R) other than their exposed perimeter. (Or you might adjust the U-value for the floor if some spaces are carpeted and others are bare concrete, for example.) I would model the proposed building with an edge insulation of R-10 and a floor slab U determined by adding the R-values for an indoor horizontal air space with heat transfer in the downward direction, average carpet or flooring you have, plus the concrete slab itself -- then taking the inverse to get U instead of R. So then the tricky part is what floor U and perimeter R to use for heat transfer equivalent to F-factor of 0.73 in the base building. From what I read on the this bulletin board link, http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-October/006392.html an F-factor of 0.73 is equivalent (at least in E-Quest) to a 6-inch thick uninsulated concrete slab with no edge insulation. So you could try using an edge R of zero and a floor U based on 6-inch thick concrete and see what result you get. Maybe do a single zone test case with a building the same area to perimeter ratio as your base building, and compare it to a manual F-factor calculation to see how close the heat loss is. Then adjust the floor U-value to get the two heat loss numbers as close as you can. This bulletin board post: http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-October/006391.html says you can convert F to edge R by multiplying the F-factor by the perimeter of the building, then dividing by the floor area of the building. Then take the inverse of that number in order to get R-value instead of U. But that seems to oversimplify for the application you have with the Carrier HAP program that also uses a floor U-value. You could also try contacting Carrier software's help desk to find out what they recommend as input for the base building 0.73 F-factor.