NC-2009 IEQc8.1:Daylight and views - daylight

Skylight coverage

Hi, in case of a not meeting the skylight coverage ratio of 3-6% for the total room space, e.g. having only 1.5%, is it possible to devide the space into two zones and include half or the room in the compliant areas, which on it's own meets the 3% skylight coverage?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/22/2014 - 20:29

If toplighting is the only source of daylight, then no. You are not meeting the requirements of the credit by possibly providing adequate daylight to the space.( I say possibly because the prescriptive method is not a determinant of adequate daylight levels or good dyalighting in general) Use simulation or measurements to document possible credit compliance. If the room also has sidelighting, then you may be able to break up the space into multiple daylight zones, dependent on the perimeter glazing, and then separate the skylights between zones.