NC-2009 IEQp2:Environmental Tobacco Smoke (ETS) control

Site plan without smoking areas

Hello LEEDusers! We are supposed to upload a site plan/map that shows the location of the designated outdoor smoking /nonsmoking areas. Since we have no smoking areas we upload a site plan highlighting only the 25ft distance from the building and position of all signs communicating the 25 ft rule. However, the building's facade is very close to the LEEDboundary. Shall we mark the non-smoking area beyond the LEEDboundary in the site plan or keep it within?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/15/2014 - 13:49

Hi Jiri, I have done dozens of projects in WA where smoking is not allowed in most places. In all cases, I have simply uploaded a statement that we have no designated smoking areas. It's a bit frustrating that item is a mandatory upload. Despite many other issues with reviewers about smoking sign verbiage and locations, no one has ever commented on that simple statement.